Any successful profibus communications from .NET?

前提是你 提交于 2019-12-02 22:59:45

We've not used Profibus, but have used DeviceNET (another CAN based protocol), Ethernet/IP and ControlNet which all have similar challenges.

We've been doing this since the late 1990's and therefore rely mainly on our own generated code using off-the-shelf hardware. The companies that have shown longevity during that period that I remember are:-

  • AnyBus (HMS, www.anybus.com) we've recently started using their gateway products as we can place fieldbus interfaces close to the hardware and then communicate over normal Ethernet (usually using Ethernet/IP www.odva.org). This has the advantage of separating hardware and PC using only a network cable. The Ethernet/IP .NET classes were written by ourselves as nothing much was on the market at the time. I'm sure a quick google search would find suitable class libraries
  • SST (www.mysst.com) have had fieldbus interfaces for more than a decade. The last SST card we used for DeviceNET still only had VB6 sample code. A good selection of fieldbus support and different form-factors e.g. PC104, PCI, PMCIA
  • Beckhoff/Wago (www.beckhoff.com, www.wago.com) we typically use Beckhoff for the I/O more than the interface cards but again a company that has been around a long time. They also have products that support exposing using OPC (another way for you to get I/O information without directly communicating with the hardware/devicedrivers)

I suggest not using OPC interfaces to the hardware directly (it’s OK for communication using PC (.NET)->PLC->Profibus) as you need to ensure that the control system responds to loss of control from your .NET application. I’m assuming that you are needing a profibus Master here (not a slave), so as long as your control system is intrinsically fail safe, then loss of communication should mean the control system enters an "Idle" state and therefore most of the I/O will return to the fails safe state.

We also try to ensure that we do not put safety related code in .NET. Most of our .NET code is userinterface from a PLC, but in some places we do control the fieldbus directly but ensure hardware interlocks will prevent un-safe operation, either using safety switches/relays or a small PLC with the the task of interlocking only. And above all make the system fail-safe! Loss of comms from the .NET code should shutdown the automation to the fail-safe state.

We have used Steeplechase to connect to our profibus to our automated pick system.

http://www.phoenixcontact.com/automation/32131_31909.htm

易学教程内所有资源均来自网络或用户发布的内容,如有违反法律规定的内容欢迎反馈
该文章没有解决你所遇到的问题?点击提问,说说你的问题,让更多的人一起探讨吧!